The Diesel Oil Service Tank Vent

Reply
 
Thread Tools
  #1  
Old 6th January 2011, 22:54
Macphail's Avatar
Senior Member
Organisation: Merchant Navy
Department: Engineering
Active: 1960 - 2002
 
Join Date: Oct 2008
Posts: 716
The Diesel Oil Service Tank Vent

The Diesel Oil Service Tank Vent Pipe..
MV Braer. Generator shutdown due to a sea water ingress into the DO service tank. Caused by heavy weather and the base of the vent pipe, situated in the upper deck scupper being rotten.

I have also experienced this on the MV “Antilochus”, 4th Engineer, sludged the DO service tank twice a day. Singapore , massive monsoon storm, rain cascading down the sides of the ship. Cargo loaded, Moved off on DO, stopped dead, the DO service tank was part full of water. On investigation it was found that the vent pipe to DO service tank had rotted away at the base.
Even in modern times, if the vent pipe lies in a scupper, it is worth a check, the diesel oil fumes are highly corrosive.

Possible, the fisher boys should check, rusty scab at the base of the vent pipe. All the best.

John.

Last edited by Macphail : 6th January 2011 at 23:14.
Reply With Quote
  #2  
Old 7th January 2011, 00:09
G0SLP G0SLP is online now  
Senior Member
Organisation: Merchant Navy
Department: Engineering
Active: 1978 - Present
 
Join Date: Sep 2007
My location
Posts: 403
Mmm, another good one is DO Service Tank sounding pipes which pass through Ballast Tanks... I took over a ship about 4 years ago; anchored for 2 days to allow the Master & myself, who'd had 3 weeks on board with the previous owners' crew, to train up our own lads. Just going round the ship with a Surveyor; all seemed OK, when the lights went out... Investigation revealed the Service Tank having lots of sea water in it - where'd it come from? Found out that the Mate, being a conscientious chap, had decided to fill & empty all the ballast tanks to check that the remote gauges worked OK. We found a 10mm diameter hole in the sounding pipe when we started looking

We were lucky it happened when it did; at anchor in a safe location, good weather & not working cargo...
__________________
Mark Coultas
Reply With Quote
  #3  
Old 7th January 2011, 15:42
R58484956's Avatar
Super Moderator
Organisation: Merchant Navy
Department: Engineering
Active: 1952 - 1965
 
Join Date: Apr 2004
Posts: 13,763
On the QE (1) in the bakers shop an oil fuel vent pipe went from floor to ceiling level thro' the shop and the shop was washed down twice a day, and the obvious happened, one day the oil went further up the pipe than usual and popped out all over the bakers floor, it was only 2"deep.Gave the lads plenty of overtime.
Reply With Quote
  #4  
Old 8th January 2011, 11:36
uisdean mor uisdean mor is offline  
Senior Member
 
Join Date: Sep 2008
Posts: 190
Another difficult one to figure out after the first instance.
Main day fuel tank vents led as high as possible and on this occassion protected "inside" emergency generator flat next to funnel. EGen room had usual watertight door and jalousie venting. Over time the practice was to keep door and jalousie closed off - wrong on a few fronts but we all know how easy it is to "get used" to what seems normal without thinking too much. Come the day when emergency generator needed in earnest it cut out soon after start up. Problem was fresh water in the fuel? Where was it coming from? Condensate from the atmosphere as warmer day tank vents drew it out of the air. A sore lesson learnt and needless to say proper ventillation and check procedures instated after the event.
Rgds
Uisdean Mor
Reply With Quote
  #5  
Old 13th January 2011, 02:33
Malky Glaister Malky Glaister is offline  
Senior Member
 
Join Date: Nov 2008
Posts: 854
I've had a several water in fuel tank problems both salt and fresh. What peed me off no end ?
It was usually laid at my door. Salt contamination of heavy fuel does the engine no good at all. Blame the Chief. (It costs a lot to debunker a ship you see but fuel injection gear well that can go on next years bill) I packed it all in after a couple of blame layings

regards Malky
Reply With Quote
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

vB code is On
Smilies are On
[IMG] code is Off
HTML code is Off

Similar Threads
Thread Thread Starter Forum Replies Last Post
Tank Cleaning d.r.wing Tankers 70 19th July 2014 01:13
Tank Ventilation Dickyboy BP Shipping 52 10th June 2010 11:40
tank you Wilson Benvenuti Jr. Say Hello 7 26th January 2009 09:58
Deep tank tragedy Port Swettenham. ian keyl Ben Line 4 26th September 2007 10:51



Search the net with ask.com
Support SN
Ask.com and get


Powered by vBulletin® Version 3.6.8
Copyright ©2000 - 2014, Jelsoft Enterprises Ltd.